Requirements for Boiler Installation Rooms
Forum
Notes on the installation of b..
Notes on the installation of boilers and boiler house11 Years AgoRequirements
for Boiler Installation Rooms
Notes on the installation of boilers
and boiler house
components
1 General
This technical information describes the requirements for
boiler installation rooms and contains notes on the installation of
boilers and boiler house components for steam, superheated
steam, warm and hot water boiler systems. It is intended to
provide assistance to planners of installation rooms and
buildings. All the relevant national and local regulations and
applicable standards should also be followed.
2 Basic requirements
for the installation room
The following basically requirements for the boiler room
must be met:
• The boiler system may only be installed in a room that
meets the local regulations for the installation of boiler systems.
• The installation room must be kept clean and free from
dust and dripping water. The inside temperature must be
between 5°C and 40°C.
If the air contains salt (proximity to the sea), the
maintenance intervals of the boiler system may be shortened.
• Unauthorised persons must be forbidden to access the
boiler room through permanent, clearly visible notices.
• Depending on the boiler parameters(water content,
pressure, capacity), less strict installation or supervisory regulations
may be applicable, depending on the national regulations.
• Sound insulation requirements must be met in accordance
with local regulations.
• The control cabinets must be installed in such a way that
no vibrations or shaking of the system components can be
transmitted to the control cabinets. Installation must be
carried out in areas which protect the control cabinets against
excessive radiated heat and which safely allow access in
situations which could be dangerous
• Free access to inspection openings on boilers and plant
components must be ensured.
2.1 Requirements on
the building
The following requirements on the building must be met:
• The place of installation must be designed in such a way,
in terms of construction, that vibrations caused by the process
cannot cause any damage to buildings or neighbouring
systems.
• The structural loading of the building shell must be taken
into consideration for all fixings.
• Every boiler installation room must have n external wall
or ceiling surface that is if possible continuous and clear,
totalling at least 1/10 of the ground surface area (or in
accordance with local requirements) which, in the event of excess
pressure in the boiler installation room, will give much
more easily than the other enclosing walls.
• The opening for brining equipment into the boiler
installation must be made in accordance with the dimensions of the
individual components. Suitable lifting equipment must be
provided in the boiler installation room for moving heaving
equipment.
• The clear height and width of all surfaces that can be
walked on must be sufficient. Access to the system must be
guaranteed in accordance with the local regulations. If the
clear height of the installation room is smaller than the
required height, for construction reasons, the minimum
height must be agreed with the local authorities.
• Suitable, clearly marked emergency rescue routes must be
provided.
• The boiler installation room, especially in the area of
the valves and safety equipment, and the emergency rescue
routes must be well lit.
• The parts of the system that are to be operated must be
easily accessed and there must be sufficient space to pen
doors (including inspection openings)
Requirements
for Boiler Installation Rooms
|